The Solar / Inverter / Power thread
- Thread starter Tag11
- Start date
Why so few panels on a big boy inverter?
The panels are what save the money and also generate ROI.
Or are they all going on one MPPT for future expansion?
Whatever is delivered from stock on the day... 1st tier only is the only promise they make, and should be one of these:What make are those panels?
555W is very high, way higher than anything i can get here.
@SauRoN
Funny, you were the one person I was planning to engage with to discuss this with.
So budget is a factor, so is roof space. We're expecting to generate about 30kwhr/day and use on average 40... I'm ok with a 75% reduction in my Eskom bill. The future planning also includes getting away from electric stove/ovens... (closer to Winter time I will review)
They will put 5 panels facing NE on one MPPT and 5 panels facing NW on the other MPPT
Depending on how they perform and what we find on the roof (numerous ridges) we might then add a few more panels to one or the other MPPT/side or somewhere else if needed later.
I engaged with Standard Bank's LookSee programme, because I got so many quotes from so many "reputable" companies and the prices fluctuated so much and they either had amazing reviews/references or the odd terrible one, so much conflicting information that in the end I wanted a big brother to oversee things. Standard Bank put me in touch with a company called Sinogy, and I was happy with what they had to offer. Plus, most of the damn independents aren't VAT registered... how do you sell multiple R100k-R300k solar solutions and escape VAT registration??? Dodgy!
Bottom line, I'm committed, but now I need to be sure this guy/company do it properly. I want everything on essential - I just don't see the point in putting my stove/oven/geyser on non-essential and then when I need them I can't tap into my battery storage. Isn't that the point of having control via an app? If I know load shedding is gonna happen at 6pm, and we need to make dinner, then surely I can decide - push all PV generation to prioritise topping-up the batteries, so that they're available for us to cook at 7pm? Right?
And if I ever exceed 8800W then it's fine, because it will draw from Eskom right? (No tripping or over loading the inverter)
And if there is load shedding, I just have to be smart and ensure we never exceed 8800W right? (Pretty easy to do - no oven/stove/hair-dryer/air-fryer/tumble-dryer during load shedding)... unless absolutely necessary, in which case I can manage it myself via the app. Also, I've added a wifi switch to my geyser, so I can turn off the geyser during LS or plan ahead and make sure it is hot before we need it. (2nd geyser is solar already)
Then there is the whole CT Coil which it seems only some installers understand how to use (I'm not entirely clear on the understanding of it myself), and also the fact that our estate uses the Conlog wireless pre-paid meter system, which also comes with some complexity which has to be considered and requires appropriate experience.
I figured a very experienced company like Sinogy would have me covered... but I'm not feeling that comfort anymore. (I've voiced my complaint, and they've assured me they will take full responsibility - I will call them back if anything isn't 100%!)
Hopefully batteries will follow, considering the lithium prices have fallen through the floor.Solar panel prices has been falling hard:
Hopefully batteries will follow, considering the lithium prices have fallen through the floor.
Solar panel prices has been falling hard:
https://leroymerlin.co.za/longi-solar-panel-mono-555w-1
This was R1900 2 weeks back.

lol maybe not heard of in Africa but they are huge over here. Rated as Tier 1 alongside Canadian, Jinko etc.Don't buy this kak nobody has ever heard of.
lol maybe not heard of in Africa but they are huge over here. Rated as Tier 1 alongside Canadian, Jinko etc.
But if the other brands are better represented locally then it’s probably worth spending a bit more on those.
Remember you can't add another direction later without another external MPPT or parellel inverter so rather plan to add more in these two directions which aren't all bad as they may extend your light hours even if peak output isn't perfect.
My Sunsynk 8kW has two MPTTs and allows two strings per MPTT. But all the panels on the same MPTT needs to face the same way (direction and angle). The reason for that is the two strings will then produce the same voltage, which is required on the same MPTT. If it faces a different direction the generation will be different and needs to be on another MPTT.Thanks... this statement is the only one I'm not clear on - are you saying if I want to add more panels later, they HAVE to point in the same direction? Because we do have a tentative upgrade plan for another 6 panels, but they would need to go on a different part of the roof.
I'm surprised I understood everything you saidMakes me feel more comfortable about the process I'm following.
Installation is happening as I type. They adding sufficient channeling to easily add a 3rd battery later. Panels delivered are JA Solar 550W
Thanks... this statement is the only one I'm not clear on - are you saying if I want to add more panels later, they HAVE to point in the same direction? Because we do have a tentative upgrade plan for another 6 panels, but they would need to go on a different part of the roof.
I'm surprised I understood everything you saidMakes me feel more comfortable about the process I'm following.
Installation is happening as I type. They adding sufficient channeling to easily add a 3rd battery later. Panels delivered are JA Solar 550W
Yes same MPPT same direction in series.
And 9-10 panels per MPPT.
Technically you could put multiple sets of panels in parallel but this is a bit of a dodgy thing where you can't have them active at once and so they need to be on two opposite extremes so one set is in the shade while the other is active.
It's one thing I would have done differently is buy 2 x 5kW inverters from the start so I have 4 x MPPTs as I need to upgrade to 2 x North 1xEast and 1xWest in the future.
That does make a lot of sense...
What is your view on using just 1 string per MPPT ? If I don't need to use 2 strings, why would I ? (only 5 panels per MPPT at the moment, which is also an odd number)