The Solar / Inverter / Power thread
- Thread starter Tag11
- Start date
Tag11
Active member
ok, so today had an anomaly, not sure why yet, have logged it with the solar provider, but they take long...
Got an overload error, and the system shutdown.

this concerns me, because we are making more than enough solar power, and we are also sitting with full SOC on our batteries (which are set to output 160A) and we are NOT load shedding. So why after a peak output of 10.92kW would the system overload and shutdown?
I thought there is supposed to be a passthrough that ensures the inverter can handle peaks of over 18kW, so long as the grid is available to supplement what we cannot provide from the battery – and it is.
Here is another report

If my panels are generating 6.5kW and my battery is outputting 1.71kW (even though my battery can do much more than that), I understand that is at the peak output of the inverter – but if there is additional demand, the Grid should provide it – as it did with another 2.92kW… so why did the system shutdown/trip??
https://lifetide.co.za/data-sheets/Deye-8kW-Datasheet.pdf according to the data sheet… the system should even be able to handle 2x the total rated powed when OFF-GRID for 10 seconds. We were on-grid, so why did it shutdown at 10.9kW ??
Would appreciate anyone's advice here...
Got an overload error, and the system shutdown.

this concerns me, because we are making more than enough solar power, and we are also sitting with full SOC on our batteries (which are set to output 160A) and we are NOT load shedding. So why after a peak output of 10.92kW would the system overload and shutdown?
I thought there is supposed to be a passthrough that ensures the inverter can handle peaks of over 18kW, so long as the grid is available to supplement what we cannot provide from the battery – and it is.
Here is another report

If my panels are generating 6.5kW and my battery is outputting 1.71kW (even though my battery can do much more than that), I understand that is at the peak output of the inverter – but if there is additional demand, the Grid should provide it – as it did with another 2.92kW… so why did the system shutdown/trip??
https://lifetide.co.za/data-sheets/Deye-8kW-Datasheet.pdf according to the data sheet… the system should even be able to handle 2x the total rated powed when OFF-GRID for 10 seconds. We were on-grid, so why did it shutdown at 10.9kW ??
Would appreciate anyone's advice here...